ronsin1 wrote:20 amp for the 12,000 BTU
30 amp for the 18,000 BTU
crossdrilled wrote:ronsin1 wrote:20 amp for the 12,000 BTU
30 amp for the 18,000 BTU
^^^ this. These are the maximum values, and once Full load current does not exceed 80% of your breaker rating, you should be fine whatever size you use. Just make sure the cable is at least 2.5mm square if it is being protected by the 20A breaker and 4mm square if being protected by the 30A breaker on a single branch.
nick009 wrote:crossdrilled wrote:ronsin1 wrote:20 amp for the 12,000 BTU
30 amp for the 18,000 BTU
^^^ this. These are the maximum values, and once Full load current does not exceed 80% of your breaker rating, you should be fine whatever size you use. Just make sure the cable is at least 2.5mm square if it is being protected by the 20A breaker and 4mm square if being protected by the 30A breaker on a single branch.
what this guy said is very important.make sure your wires are sized correctly. Breakers are to protect the wires not so much the equipment.
sizzla89 wrote:nick009 wrote:crossdrilled wrote:ronsin1 wrote:20 amp for the 12,000 BTU
30 amp for the 18,000 BTU
^^^ this. These are the maximum values, and once Full load current does not exceed 80% of your breaker rating, you should be fine whatever size you use. Just make sure the cable is at least 2.5mm square if it is being protected by the 20A breaker and 4mm square if being protected by the 30A breaker on a single branch.
what this guy said is very important.make sure your wires are sized correctly. Breakers are to protect the wires not so much the equipment.
Are you serious? Breakers are designed to provide that safety factor between increasing load within the circuitry, due to whatever reasons. They should trip once that tolerance has been exceeded.
I am not saying that the wire size is not important. However once it is properly selected the breaker is mainly designed as a measure to prevent over loading of currents within equipment attached to the circuit. Improper usage of these can result in electrical fires within equpiment and burning of wires etc.
wheelbarrow wrote:OP the electrical inspectorate advises that in a residential application that size AC should use a 30 amp breaker and 4.0mm wire. Also the breakers are there to protect the wire that is connected to it. [/thread]
wheelbarrow wrote:OP the electrical inspectorate advises that in a residential application that size AC should use a 30 amp breaker and 4.0mm wire. Also the breakers are there to protect the wire that is connected to it. [/thread]
crossdrilled wrote:^^^^Annex c to be precise.
Sasquat007 wrote:jus remember fastest thing to out electrical fire is red sand so keep some close by !
as ah man say here 30A for ac units and water heaters !
crossdrilled wrote:Sasquat007 wrote:jus remember fastest thing to out electrical fire is red sand so keep some close by !
as ah man say here 30A for ac units and water heaters !
Reading these two statements I was like:
~Vēġó~ wrote:too much headache...buy ah 2-3 lasko fan
rfari wrote:sizzla89 wrote:nick009 wrote:crossdrilled wrote:ronsin1 wrote:20 amp for the 12,000 BTU
30 amp for the 18,000 BTU
^^^ this. These are the maximum values, and once Full load current does not exceed 80% of your breaker rating, you should be fine whatever size you use. Just make sure the cable is at least 2.5mm square if it is being protected by the 20A breaker and 4mm square if being protected by the 30A breaker on a single branch.
what this guy said is very important.make sure your wires are sized correctly. Breakers are to protect the wires not so much the equipment.
Are you serious? Breakers are designed to provide that safety factor between increasing load within the circuitry, due to whatever reasons. They should trip once that tolerance has been exceeded.
I am not saying that the wire size is not important. However once it is properly selected the breaker is mainly designed as a measure to prevent over loading of currents within equipment attached to the circuit. Improper usage of these can result in electrical fires within equpiment and burning of wires etc.
breakers is to protect the conductors. what defines an overload? not the rating of the conductor and the breaker?
Around wrote:nice to see some men got the ttbs low voltage to advise the rest