pugboy wrote:marvy report say wires from one circuit bust and fall on a next set of wires causing a short out
how they preventing this in future
bluefete wrote:pugboy wrote:marvy report say wires from one circuit bust and fall on a next set of wires causing a short out
how they preventing this in future
People really believe this? Really?
Carry on then.
Eh?De Dragon wrote:bluefete wrote:pugboy wrote:marvy report say wires from one circuit bust and fall on a next set of wires causing a short out
how they preventing this in future
People really believe this? Really?
Carry on then.
Only stupid LFD RFD like Colos,wing and mero
st7 wrote:current gone in chaguanas area.
not sure if another blackout again lol
daring dragoon wrote:anyone getting dips in the current? lights flickering, etc. general low voltage situation.
daring dragoon wrote:anyone getting dips in the current? lights flickering, etc. general low voltage situation.
Yea, I had to call them this week. Voltage spiking to 312V, not a one off eventst7 wrote:daring dragoon wrote:anyone getting dips in the current? lights flickering, etc. general low voltage situation.
i been noticing spikes the last few weeks (chaguanas area).
mamoo_pagal wrote:Yea, I had to call them this week. Voltage spiking to 312V, not a one off eventst7 wrote:daring dragoon wrote:anyone getting dips in the current? lights flickering, etc. general low voltage situation.
i been noticing spikes the last few weeks (chaguanas area).
Duane 3NE 2NR wrote:A tree!
This really is not a real place
1. The Palmiste tree eventually fell off the 12 KV line causing the line to sag, oscillate and upswing, and to come into contact with the 220KV line circuit, which transmits most of the power from the TGU generating facility to T&TEC. The 12 KV line crosses orthogonally under the 220 KV transmission by a distance of over four (4) metres, which is more than two times the minimum stipulated by international standards.
2. The fault occasioned by the two lines accidentally coming into contact with each other caused the protection relays on the two circuits on the 220 KV transmission line to trip sequentially and become de-energised thereby isolating the TGU plant from the grid.
3. The de-energizing of the 220 KV transmission line, created a large imbalance between available running generation supply (537 MW) and load (68.75 MW) resulting in a very rapid increase in generation speeds at the TGU plant, as the essentially unloaded turbines accelerated. The turbines immediately tripped on over speed protection, disconnecting all generators at TGU thereby resulting in a 47% loss of generating capacity.
4. The sudden loss of 47% of generating capacity on the grid was too fast for the system’s circuit breakers to shed load to match the available generation. In the circumstances, the other IPPs experienced underspeed and under-frequency conditions which exceeded their stability limits leading to a cascading outage and the collapse of the entire electricity grid, first at the Point Lisas plants and then at Penal.
https://trinidadexpress.com/newsextra/c ... 73038.html