Send a sketch. Or better yet send the actual schematic. From what you described this may not be normal but a sketch is the best way to help you out.nervewrecker wrote:One for the techs in here.
3 phase system, red, yellow and blue wires.
The main breaker supplies 2 3 pole breakers for isolators, one for air handler and one for condenser.
Condenser has a double pole contactor supplying split phase induction type fan motor and three phase compressor, blue line hooked up direct with a lug, red and yellow on line side of contactor, red and yellow on load side of the contactor.
Fan works with yellow wire disconnected from load side of the contactor, contactor coil not energised, not closed.
Works only when condensor isolator is turned on.
Leme hear allyuh...
nervewrecker wrote:One for the techs in here.
3 phase system, red, yellow and blue wires.
The main breaker supplies 2 3 pole breakers for isolators, one for air handler and one for condenser.
Condenser has a double pole contactor supplying split phase induction type fan motor and three phase compressor, blue line hooked up direct with a lug, red and yellow on line side of contactor, red and yellow on load side of the contactor.
Fan works with yellow wire disconnected from load side of the contactor, contactor coil not energised, not closed.
Works only when condensor isolator is turned on.
Leme hear allyuh...
nervewrecker wrote:I will video it.
Having a hard time understanding how a fan coming on with no power to it (contactor open) and one line disconnected.
I'm getting continuity to ground on the yellow phase with the isolator on though.
Have to check the load cable from the panel breaker to the isolator to see if that damaged and getting continuity to ground there. I made a mistake and checked to ground on the line side of the contactor and the yellow phase read continuity.
will update on details tomorrow, wanna sleep.
Got shocked with the red phase on the load side of the contactor and dismissed it as the capacitor from the fan.
Got shocked again so I assume the contactor closed, took off the cover and it was open. Checked continuity between line and load on each pole, none. Checked to ground (both sides) yellow reads continuity on line side. Thats how I checked continuity by mistake while live.
Got shocked with the signal line for the contactor coil, one side reads 54 V to ground. Air handler off so no signal / voltage should be there.
nervewrecker wrote:Blue phase took some heat at one point, insulation burned off.
Another system, isolator burned up badly. Lug welded to ground from arcing.
hong kong phooey wrote:nervewrecker wrote:One for the techs in here.
3 phase system, red, yellow and blue wires.
The main breaker supplies 2 3 pole breakers for isolators, one for air handler and one for condenser.
Condenser has a double pole contactor supplying split phase induction type fan motor and three phase compressor, blue line hooked up direct with a lug, red and yellow on line side of contactor, red and yellow on load side of the contactor.
Fan works with yellow wire disconnected from load side of the contactor, contactor coil not energised, not closed.
Works only when condensor isolator is turned on.
Leme hear allyuh...
ok you probably heard of single phasing. most 3 phase motors with pump and other high torque starting applications will not start but you would hear a loud hum, but because a fan is already turning it will start to run but it is very loud most times. you can hear the difference in the motor.
from what you describe for this to occur this means your contactor(red phase) is welded together or it has arc enough to be touching on each side
this can occur when you have higher current than the contactor is what we call chattering dropping in and out.
Best bet is to open the contactor and clean the poles . Then once the contacts are not touching any more the fan will not run with the yellow phase disconnected.
This system seems very shoddy. This is why I told you, you need to test each system with a meter. Loads of times we say to ourself the motor/equipment not energised because the contactor open, but here we can clearly see this one is not the case. the blue wire is always energised once the breaker is closed.
the same which happens to the contactor can also happen to a breaker (although much less likely) so it is important to always check with your meter that you have no voltage when you open the breaker.
This seems to be calling grounding, earthing and bonding the same thing.carluva wrote:So my friend you and some of the other posters have the general gist, but allow me to clarify a few areas which should help younto understand grounds...maj. tom wrote:nervewrecker wrote:Something I am having a hard time understanding and its best I ask here one time:
When you on the ground and you touch a conductor that is carrying current to ground you can get shocked. Arent, you at the same potential to ground and your internal resistance is more than that of the conductor? I understand you wont get the full dose but if you hold a current wire and not touching the ground you don't get shocked. Same way birds dont get shocked.
Well you're right, as far as I understand it also.
If you touch a ground wire that's carrying current to the ground you can get a shock if you are in direct uninsulated contact (barefoot) with the ground. Some amount of current will flow through you and the ground if you are barefoot because you are creating an electrical potential difference between two points. When you are in contact with the ground barefoot you are not really grounded at the same potential as the ground because you are mostly made of water and that creates resistance and thus a potential difference in the circuit. Most of the current will continue to flow in the ground wire. But it only takes 0.1 A flowing across the heart's sinus node to cause atrial fibrillation and a heart attack. If you're wearing proper insulated work boots it should not happen. Always check that your boots are not penetrated by a nail or anything metal. Also there's a standard in the depth they use for ground rods for a reason. http://www.cpuc.ca.gov/gos/GO95/go_95_rule_59_4.html
Current can only flow when there is an electrical potential difference between two points. A bird can't get shocked because all the touching points are the same voltage. If the bird's wing touched another wire while sitting on the bottom wire, it will fry. Because potential difference.
Grounding really means equalizing the voltage across two points. You ever saw videos of helicopter linemen grounding off by attaching the wire to the helicopter first? They're equalizing the voltage across those two points, so now the lineman has no potential difference between him and the wire.
An airplane has static wicks/pins attached all over points on the body and wings that discharges any buildup of electricity that occurs due to lightning or just due to a metal object moving through a magnetic field. The fuselage is designed to act as a Faraday cage to protect everything inside. After a lightning strike they will ground the plane and go over every system with a fine tooth comb before allowing it to fly again.
I never really studied the topic as I'm not an electrical engineer, so disclaimers on that, and willing to be corrected by those who know better.
Grounding does not mean to equalise voltage. The purpose of grounding is to create the path of least resistance for electricity (ie current) to flow in the event that electricity wants to flow anywhere else but within its intended conductors. When current begins to flow in a ground circuit, a potential difference is created.
Secondly, nerve, let me clarify another area. Current does not normally flow in a ground. Current only flows in a ground when there is a ground fault or in other words a part for current to flow through ground. If you ever come across circuits where there is a current in the ground, you have a ground fault. This is why in a properly wired house, you can handle the ground wire with no worries because there will never be current in the ground. Try handling the live wire and you'll get shocked. You can also handle the neutral of a single circuit and not get shocked because neutral is usually grounded in our homes.
So that's why we have GFCI outlets.... In the event that an item is plugged into a GFCI and that item develops a short, ie, a current flow to ground, the GFCI trips to protect the circuit. These are usually resettable. That's why in wet areas like kitchen and bath, GFCIs are mandatory cause the exposure of using an electrical item close to water causes a lower resistance path to ground, due to the water, and increases the likelihood of a ground fault.
This sounds very much like an earth fault in that one of the phases are shorting to ground.nervewrecker wrote:I will video it.
Having a hard time understanding how a fan coming on with no power to it (contactor open) and one line disconnected.
I'm getting continuity to ground on the yellow phase with the isolator on though.
Have to check the load cable from the panel breaker to the isolator to see if that damaged and getting continuity to ground there. I made a mistake and checked to ground on the line side of the contactor and the yellow phase read continuity.
will update on details tomorrow, wanna sleep.
Got shocked with the red phase on the load side of the contactor and dismissed it as the capacitor from the fan.
Got shocked again so I assume the contactor closed, took off the cover and it was open. Checked continuity between line and load on each pole, none. Checked to ground (both sides) yellow reads continuity on line side. Thats how I checked continuity by mistake while live.
Got shocked with the signal line for the contactor coil, one side reads 54 V to ground. Air handler off so no signal / voltage should be there.
carluva wrote:Grounding and earthing is the same exact thing.
Bonding has different meanings but when applied to earth, yes, bonding would mean the same. Bonding is actually the connection of a conductor to ground/earth.
No timer, timer is on air handler control section. 3 minute time delay to turn on load so as to not have it start on high head pressure. This circuit is on the contactor coil.hong kong phooey wrote:Nerve is there a timer in the circuit ?
Normally there is a circuit diagram stuck to the lid of the control box , do you have a picture of that?
is the fan spinning at full speed
this fan is a single phase fan , your compressor is a 3 phase compressor
what you have is a start and run winding on your fan but it is a single phase
trace the wires going to the fan see if there is any relay or another contactor or timer in the cct.
nervewrecker wrote:No timer, timer is on air handler control section. 3 minute time delay to turn on load so as to not have it start on high head pressure. This circuit is on the contactor coil.hong kong phooey wrote:Nerve is there a timer in the circuit ?
Normally there is a circuit diagram stuck to the lid of the control box , do you have a picture of that?
is the fan spinning at full speed
this fan is a single phase fan , your compressor is a 3 phase compressor
what you have is a start and run winding on your fan but it is a single phase
trace the wires going to the fan see if there is any relay or another contactor or timer in the cct.
No other control devices.
Had a line monitor but that seems to have been condemned.
Fan motor is single phase 220v and it does not spin full speed.
As soon as the isolator turn on you get a burning scent.
nervewrecker wrote:What im also not getting is if there is an earth fault on the yellow why am I not getting 220v on the blue and red when measured to ground?
nervewrecker wrote:I am also thinking its the blue phase going through the comp motor windings and coming back to the load side of the contactor.
Of course look at your drawing the blue phase will go through your compressor and come back on your other 2 phases . it going to pass through the coil of your compressor and to the red and yellow phases . Remember this is AC the voltage is a sine wave.
When I got shocked from the red load side of the contactor with it disconnected and breaker off it may have been the fan capacitor discharging.
But im curious as to whats completing the circuit for the fan as it will be the blue phase 208v going to the comp coil and coming back to the yellow on the load sode of the contactor so im getting a 208v (neglecting losses due to resistance across the comp coil) one line on the fan motor. But whats completing the circuit?
See my post above
the red wire has to be toughing earth somewhere and most likely where u smelling the burning
The second line is disconnected and not connected anywhere. Im thinking that red line from the fan is pinched somewhere and touching the body so its making a ground and completing the circuit as the wire end is loose and hanging mid air. Either that or the motor winding insulation damaged and its going to ground somewhere.
Burnt scent not coming from the motor. Coming from the wires from the isolator to the line side of the contactor.
The earth fault on the yellow phase between main breaker to isolator will explain thr 54V on the signal wire as its one line live and an inline relay on the next to give a 220v to close the contactor coil on the air handler side.
Taxpayers money paid for this sh11ty wiring I should add. Such a disgrace.
In your defence, the blower motor should not have been directly wired to any supply if there was to be shutoff controlled by the contactor.nervewrecker wrote:Haven't went back yet. Someone is questioning me and what I know, seems that person knows more than me.
Probably want to spend some money and let their pple get the job to supply new stuff. And when they f**k it up I still have to come fix it just like with every other piece.
As far as I concerned, this system looks ok to startup, its an electrical issue. Thats EFCL area, I cant keep doing their work for them .